Big linear bench PSU trips RCD at turn on or off
I got immense help from here fixing up my old Farnell 60V @ 50A variable bench linear supply and it's keeping my shack warm nightly powering a 1kW amp TX'ing on LF
It has one annoying trait though. Quite often at power on or power off from the dual pole PSU panel mains switch it trips the mains distribution panel 30mA RCD. I suspect it may be something to do with the filter caps and huge choke on the mains input to the supply. Is there a fix, it's a PITA both running up and downstairs to reset the RCD, and for the earache I get from the wife as her "whatever TV trash of the moment" is interrupted? I attach the relevant part of the schematic below, the input caps values are to the right, thanks. Supply is on UK mains 230V at 50 Hz. A full size version of the schematic is at http://www.gatesgarth.com/H60001.jpg
__________________
Best Regards, CW. 2E0ILY Last edited by Chris Wilson; 13th Dec 2017 at 3:08 pm. |
13th Dec 2017, 3:04 pm | #2 |
Moderator
Join Date: Jan 2003
Location: Ipswich, Suffolk, IP4, UK.
Posts: 21,289
|
Re: Big linear bench PSU trips RCD at turn on or off
I'd be inclined to get the unit P.A.T tested, or do your own test using a Megger to make sure there no problem with C21 and C22 leaking. These should be Class Y caps.
__________________
Graham. Forum Moderator Reach for your meter before you reach for your soldering iron. |
13th Dec 2017, 3:06 pm | #3 |
Heptode
Join Date: Feb 2006
Location: Marlborough, Wiltshire, UK.
Posts: 917
|
Re: Big linear bench PSU trips RCD at turn on or off
It will have earth leakage by design as the two input caps from live and neutral will produce it (they will not cancel out as live is much further from earth than neutral of course). The only thing I can suggest is to reduce the value of these input caps, at the expense of reduced rf suppression. "Low leakage/medical grade kit" usually omits these caps but take considerable other measures of course. It is worth checking the caps for value and leakage if you can, in case they are damaged.
Ken |
13th Dec 2017, 3:11 pm | #4 |
Banned
Join Date: Dec 2013
Location: Middlewich, Cheshire, UK. & Winter in the Philippines.
Posts: 3,897
|
Re: Big linear bench PSU trips RCD at turn on or off
A slow start circuit using a series ballast resistor and relay over ride will solve the problem if the PSU will cope with a slow start.
This is a problem with large transformers such as welders and isolating transformers. In fact there was a recent thread on this subject with such a transformer. But it was MCB tripping. https://www.vintage-radio.net/forum/...d.php?t=127334 Is your RCD actually an RCBO? RCDs do nuisance trip with transformer loads, my welder does it and there is nothing wrong with it. Last edited by Boater Sam; 13th Dec 2017 at 3:17 pm. Reason: Added |
13th Dec 2017, 3:15 pm | #5 | |
Moderator
Join Date: Jun 2003
Location: Oxford, UK
Posts: 27,969
|
Re: Big linear bench PSU trips RCD at turn on or off
Quote:
You could also use a plug in RCD adapter, which will hopefully prevent the consumer unit RCD tripping and keep the missus happy. |
|
13th Dec 2017, 3:16 pm | #6 | |
Dekatron
Join Date: Jan 2005
Location: Oxford, UK.
Posts: 17,864
|
Re: Big linear bench PSU trips RCD at turn on or off
Quote:
|
|
13th Dec 2017, 3:17 pm | #7 |
Dekatron
Join Date: Jan 2005
Location: Oxford, UK.
Posts: 17,864
|
Re: Big linear bench PSU trips RCD at turn on or off
From what I've read here, that trick doesn't usually work, unless you plug the RCD adaptor into a non-RCD-protected socket, of course.
|
13th Dec 2017, 3:18 pm | #8 |
Moderator
Join Date: Jan 2003
Location: Ipswich, Suffolk, IP4, UK.
Posts: 21,289
|
Re: Big linear bench PSU trips RCD at turn on or off
At least with this thread we know exactly what's tripping ie the RCD. Often we read "the mains trips" without any indication as to whether it's the RCD or MCB.
__________________
Graham. Forum Moderator Reach for your meter before you reach for your soldering iron. |
13th Dec 2017, 3:19 pm | #9 |
Dekatron
Join Date: Apr 2012
Location: Worksop, Nottinghamshire, UK.
Posts: 5,554
|
Re: Big linear bench PSU trips RCD at turn on or off
The circuit diagram is showing a soft start circuit on the mains side of the big transformer.
Some big power supplies just have filter caps that are simply too big for the RCCD. |
13th Dec 2017, 3:20 pm | #10 | |
Moderator
Join Date: Jan 2003
Location: Ipswich, Suffolk, IP4, UK.
Posts: 21,289
|
Re: Big linear bench PSU trips RCD at turn on or off
Quote:
__________________
Graham. Forum Moderator Reach for your meter before you reach for your soldering iron. |
|
13th Dec 2017, 3:36 pm | #11 |
Tetrode
Join Date: Mar 2017
Location: Dublin, Ireland
Posts: 75
|
Re: Big linear bench PSU trips RCD at turn on or off
If you fancy a little DIY, then Boater Sam's suggestion should work nicely. If you need more detail then I highly recommend this (excellent) youtube video: https://www.youtube.com/watch?v=_pEmpvcNmXg
It shows the issue you're having and a practical inrush current limiting circuit. Regards. D. |
13th Dec 2017, 3:38 pm | #12 |
Moderator
Join Date: Jan 2003
Location: Ipswich, Suffolk, IP4, UK.
Posts: 21,289
|
Re: Big linear bench PSU trips RCD at turn on or off
The problem here is not in-rush current. As has been pointed out, the PSU has a soft start circuit built in.
__________________
Graham. Forum Moderator Reach for your meter before you reach for your soldering iron. |
13th Dec 2017, 3:41 pm | #13 |
Nonode
Join Date: Jan 2010
Location: North Somerset, UK.
Posts: 2,130
|
Re: Big linear bench PSU trips RCD at turn on or off
Several options.
Run a non RCD supply to the point of use and add a local RCD at the point of use, this will be just as liable to trip but may be reset with minimal trouble. If the incoming supply is TT, making an RCD at the supply end mandatory, then use a time delayed 100ma RCD at the mains incomer and a quick acting 30ma RCD at the point of use, where it can be readily reset. Some RCDs are liable to trip on large surge or inrush currents even without any earth leakage. Test for this by connecting the power supply to the mains via several long extension leads as a test. If the extra resistance thus introduced cures the RCD tripping, then some form of inrush current limiter is called for. As has already been suggested, temporarily remove the mains input filter caps to see if this cures the problem. |
13th Dec 2017, 3:43 pm | #14 |
Moderator
Join Date: Jan 2003
Location: Ipswich, Suffolk, IP4, UK.
Posts: 21,289
|
Re: Big linear bench PSU trips RCD at turn on or off
Indeed. Find out what the problem is before prescribing a cure.
__________________
Graham. Forum Moderator Reach for your meter before you reach for your soldering iron. |
13th Dec 2017, 3:49 pm | #15 |
Banned
Join Date: Dec 2013
Location: Middlewich, Cheshire, UK. & Winter in the Philippines.
Posts: 3,897
|
Re: Big linear bench PSU trips RCD at turn on or off
This is a need to know.
An RCD is a trip that simply works if the live and neutral are not in balance. An RCBO is the same BUT it also is an over current trip like an MCB in the same item. RCDs and RCBOs in series can trip in whatever order they feel like, a real pain. If possible keep to one on a circuit only. I have never worked out why my welder trips the RCD on power up sometimes and not others, it is not faulty, just a big inductive load until the transformer saturates. |
13th Dec 2017, 4:06 pm | #16 |
Heptode
Join Date: Nov 2011
Location: Whitchurch, Shropshire, UK.
Posts: 612
|
Re: Big linear bench PSU trips RCD at turn on or off
It's a plain vanilla RCD, but why as often as not, does this thing trip the RCD on turn *OFF* as well? Thanks for the replies so far. Oh, and it is already on a fairly long extension lead, but it's a very hefty one with 16 Amp plugs and sockets. I will remove the earth connection from the two caps and see what it does. I may just fit a higher mA RCD for the supply to the "shack", and give it its own panel.
__________________
Best Regards, CW. 2E0ILY |
13th Dec 2017, 4:09 pm | #17 |
Dekatron
Join Date: Apr 2011
Location: Cornwall, UK.
Posts: 13,454
|
Re: Big linear bench PSU trips RCD at turn on or off
Y caps are a path to earth, both switch poles won't open or close at exactly the same time.
Just thinkin' here. Lawrence. |
13th Dec 2017, 4:13 pm | #18 |
Heptode
Join Date: Nov 2011
Location: Whitchurch, Shropshire, UK.
Posts: 612
|
Re: Big linear bench PSU trips RCD at turn on or off
Actually, you may well have a good point there Lawrence, I used to think it did this less if I flicked the switch with some gusto...
__________________
Best Regards, CW. 2E0ILY |
13th Dec 2017, 6:13 pm | #19 |
Dekatron
Join Date: Apr 2012
Location: Worksop, Nottinghamshire, UK.
Posts: 5,554
|
Re: Big linear bench PSU trips RCD at turn on or off
The test for that would be to swap L and N at both sides of the power switch in the PSU.
|
13th Dec 2017, 6:18 pm | #20 |
Moderator
Join Date: Jan 2003
Location: Ipswich, Suffolk, IP4, UK.
Posts: 21,289
|
Re: Big linear bench PSU trips RCD at turn on or off
I can't see why that would help. An RCD detects a difference in currents in the L and N wires. It does not have an earth connection, so cannot directly detect current flowing to earth.
__________________