Transformer voltages?
Hi
Can someone please help me out here I think my brain has ceased to function. Consider a transformer with connections 0v, 240v and 400v on the primary and a 24v secondary. If 400v was connected between the 240 and 400v terminals what would the OP volts be? Would it be 60v thanks Mike |
17th Oct 2020, 4:02 pm | #2 |
Octode
Join Date: Dec 2017
Location: Morden, Surrey, UK.
Posts: 1,558
|
Re: transformer
Briefly.....
|
17th Oct 2020, 4:04 pm | #3 |
Rest in Peace
Join Date: Mar 2011
Location: Basildon, Essex, UK.
Posts: 4,100
|
Re: transformer
Sorry when you say briefly do you mean the OP would be 60v before the primary fused itself which I presume would be fairly rapidly .
Thanks Mike |
17th Oct 2020, 4:26 pm | #4 |
Rest in Peace
Join Date: Mar 2011
Location: Basildon, Essex, UK.
Posts: 4,100
|
Re: transformer
I just hasten to add this is not something I am proposing to do. I am just confirming the likely outcome and cause of a fault with a friends piece of industrial equipment.
Mike |
17th Oct 2020, 4:52 pm | #5 |
Moderator
Join Date: Mar 2012
Location: Fife, Scotland, UK.
Posts: 22,876
|
Re: transformer
I wouldn't expect the secondary to get up to the calculated voltage because the core is likely to saturate long before. You're applying 400v to a 160v winding, 2.5 times the intended voltage.
When the core saturates the primary inductance plunges and the primary current goes through the roof. It's a race between a fuse and the wire going first. David
__________________
Can't afford the volcanic island yet, but the plans for my monorail and the goons' uniforms are done |
17th Oct 2020, 4:57 pm | #6 |
Rest in Peace
Join Date: Mar 2011
Location: Basildon, Essex, UK.
Posts: 4,100
|
Re: transformer
I have suggested to my mate he should check the continuity of all the relay windings that the transformer was supplying.
Thanks Mike |
17th Oct 2020, 7:26 pm | #7 |
Rest in Peace
Join Date: Jun 2006
Location: Chard, South Somerset, UK.
Posts: 7,457
|
Re: Transformer voltages?
I've just done the arithmetic: result = 60v. A theoretical result, of course.
Al. |
18th Oct 2020, 1:07 am | #8 |
Nonode
Join Date: Jan 2010
Location: North Somerset, UK.
Posts: 2,129
|
Re: Transformer voltages?
Yes about 60 volts IN THEORY. In practice the transformer would draw a grossly excessive current due to magnetic saturation, and would either be destroyed, or might be saved by prompt operation of the fuse or circuit breaker protecting the primary winding.
If this is an accident that has actually occurred, rather than a theoretical discussion, then relay windings would PROBABLY have survived the very brief over voltage. If the transformer looks undamaged and still works, it was probably saved by prompt operation of the fuse or circuit breaker. If future failure of the transformer or the relay coils/other loads powered by the transformer would put human life at risk, or be exceedingly costly then I would advise replacement. For less critical applications that is probably extravagant. |