UK Vintage Radio Repair and Restoration Powered By Google Custom Search Vintage Radio and TV Service Data

Go Back   UK Vintage Radio Repair and Restoration Discussion Forum > Specific Vintage Equipment > Vintage Test Gear and Workshop Equipment

Notices

Vintage Test Gear and Workshop Equipment For discussions about vintage test gear and workshop equipment such as coil winders.

Closed Thread
 
Thread Tools
Old 18th Jul 2019, 11:27 am   #41
dave cox
Nonode
 
dave cox's Avatar
 
Join Date: Jan 2009
Location: Bristol, UK.
Posts: 2,061
Default Re: Isolation/isolating transformers

I can see that by using an isolation transformer you will bypass any existing RCD so you might consider it more dangerous. For sure, there are some scenarios where that would be true but conversely in some scenarios it might be safer with a energy limited / floating supply. If you ground some part of the circuit (for measurement or it happens accidentally) then this floating advantage is defeated.

An alternative would be putting an RCD on the secondary side of and isolating transformer but also ground the secondary BEFORE the RCD. This would give you a virtual live / neutral set up, with RCD protection, but with a lot less energy available. It would be possible to do earth referenced measurement (on ac side) as long as very little current flows into the earthed point, since it bypasses the RCD. Moving the earth point to a centre tap would half the voltage available for a shock.

dc
dave cox is offline  
Old 18th Jul 2019, 11:34 am   #42
GrimJosef
Dekatron
 
Join Date: Sep 2007
Location: Oxfordshire, UK.
Posts: 4,311
Default Re: Isolation/isolating transformers

Quote:
Originally Posted by stuarth View Post
... An RCD will limit the duration of an electric shock in some circumstances where in the same circumstances an isolation transformer will prevent the shock occurring at all. In other circumstances, neither will save you from a shock.
You have described two classes of circumstances there.

Quote:
The other big advantage of an isolation transformer is that it allows you to connect earthed test gear to a live chassis set.
This generates a third class of circumstances. Now if you touch some parts of the set you can get an electric shock via the earth path that you have created with your test gear, and the RCD will not protect you.

Cheers,

GJ
__________________
http://www.ampregen.com
GrimJosef is offline  
Old 18th Jul 2019, 12:22 pm   #43
Brian of Romsey
Triode
 
Join Date: Jul 2017
Location: Fairfield, Melbourne, Australia
Posts: 48
Default Re: Isolation/isolating transformers

Further more, it is useful to remember (from a DIY & bodging perspective) at any pair of identical transformers can be back-to-backed to make a 1:1 isolation unit. It doesn't matter what the secondary voltage is really.

A second useful tip is that small low voltage transformers can be used in this sort of situation to tweak the output voltage up or down a small amount. This is done by putting the secondary in series with the main transformer's primary (and the little transformer's primary across the mains). Depending on the phase of the small transformer's secondary with respect to the main transformer's primary there is either an additive or subtractive effect. Important to ensure that the small transformer's secondary current rating is at or above the main transformer's primary current. Example: Main transformer is 500 VA so primary current will be a bit over 2 Amps, so a 6.3 V, 3 Amp transformer will do the job and will give +/- (6.3 / 230) which is about 2.7%. A 12 V transformer gives about 5%.
See https://www.youtube.com/watch?v=ZEFVNFyG9po
http://electricalacademia.com/transf...ing-principle/
https://www.mig-welding.co.uk/forum/...p-mains.38115/
http://www.dms-audio.com/bucking-transformer-diy
https://cdn.instructables.com/F12/9C...=webp&crop=3:2
Brian of Romsey is offline  
Old 18th Jul 2019, 4:13 pm   #44
stuarth
Heptode
 
Join Date: Feb 2010
Location: Heysham, Lancashire, UK.
Posts: 668
Default Re: Isolation/isolating transformers

For the thirst class of circumstances you need the isolating transformer, otherwise the RCD will trip as soon as you connect you test gear earth anywhere in the live chassis circuit.

Stuart
stuarth is offline  
Old 18th Jul 2019, 5:29 pm   #45
Sinewave
Octode
 
Sinewave's Avatar
 
Join Date: May 2016
Location: Oxfordshire/Bucks borders, UK.
Posts: 1,604
Default Re: Isolation/isolating transformers

Quote:
Originally Posted by GrimJosef View Post
Quote:
Originally Posted by stuarth View Post
... An RCD will limit the duration of an electric shock in some circumstances where in the same circumstances an isolation transformer will prevent the shock occurring at all. In other circumstances, neither will save you from a shock.
You have described two classes of circumstances there.

Quote:
The other big advantage of an isolation transformer is that it allows you to connect earthed test gear to a live chassis set.
This generates a third class of circumstances. Now if you touch some parts of the set you can get an electric shock via the earth path that you have created with your test gear, and the RCD will not protect you.

Cheers,

GJ
This is a very good point.
__________________
Avometer, vintage Fluke and Marconi collector. Also interested in vintage Yaesu and KW.
Sinewave is offline  
Old 18th Jul 2019, 5:49 pm   #46
usradcoll1
Heptode
 
Join Date: Mar 2017
Location: Cedar Grove, Wisconsin, USA.
Posts: 823
Default Re: Isolation/isolating transformers

Quote:
Originally Posted by stuarth View Post
For the thirst class of circumstances you need the isolating transformer, otherwise the RCD will trip as soon as you connect you test gear earth anywhere in the live chassis circuit.

Stuart
I understand an RCD can be located on the mains that feed the workshop alone, instead of depending on the one in the CU.
In the US, they're very reasonably priced, of course it doesn't eliminate the need of an isolation transformer. I use both! I float all my test equipment from earth by using a 3 to 2 prong adaptor, as I feel using an isolation transformer plus an RCD eliminates a great deal of hazard.
In the US, our RCD is known as a GFCI. Ground Fault Current Interrupter.
You can install as many as you want or need.
usradcoll1 is offline  
Old 18th Jul 2019, 7:25 pm   #47
GrimJosef
Dekatron
 
Join Date: Sep 2007
Location: Oxfordshire, UK.
Posts: 4,311
Default Re: Isolation/isolating transformers

Quote:
Originally Posted by stuarth View Post
For the thirst class of circumstances you need the isolating transformer, otherwise the RCD will trip as soon as you connect you test gear earth anywhere in the live chassis circuit.

Stuart
Yes. The point I was trying to make was that using the isolation transformer, which you have to if your test gear earth can't be lifted, can expose you to more danger than you were exposed to without it. It's convenient (you might say necessary for certain test gear). But it isn't a safety device - if anything it can be the opposite.

VB
__________________
http://www.ampregen.com
GrimJosef is offline  
Old 24th Jul 2019, 4:29 pm   #48
usradcoll1
Heptode
 
Join Date: Mar 2017
Location: Cedar Grove, Wisconsin, USA.
Posts: 823
Default Re: Isolation/isolating transformers

Quote:
Originally Posted by Brian of Romsey View Post
Further more, it is useful to remember (from a DIY & bodging perspective) at any pair of identical transformers can be back-to-backed to make a 1:1 isolation unit. It doesn't matter what the secondary voltage is really.

A second useful tip is that small low voltage transformers can be used in this sort of situation to tweak the output voltage up or down a small amount. This is done by putting the secondary in series with the main transformer's primary (and the little transformer's primary across the mains). Depending on the phase of the small transformer's secondary with respect to the main transformer's primary there is either an additive or subtractive effect. Important to ensure that the small transformer's secondary current rating is at or above the main transformer's primary current. Example: Main transformer is 500 VA so primary current will be a bit over 2 Amps, so a 6.3 V, 3 Amp transformer will do the job and will give +/- (6.3 / 230) which is about 2.7%. A 12 V transformer gives about 5%.
See https://www.youtube.com/watch?v=ZEFVNFyG9po
http://electricalacademia.com/transf...ing-principle/
https://www.mig-welding.co.uk/forum/...p-mains.38115/
http://www.dms-audio.com/bucking-transformer-diy
https://cdn.instructables.com/F12/9C...=webp&crop=3:2
Way back in the day, when my age was 8 or 9 YO, I'm 74 now, I had a Library book with all electrical experiments for beginners. It showed a hookup with two bell ringing transformers connected sec-to-sec. I didn't have two bell transformers, so I used an electric train transformer as the first transformer. A pleasing option is that it could be used as a form of variac. It couldn't be used for large loads, but it should've been enough for a 4 or 5 tube AC-DC set.
Dave, US radcoll1 .
usradcoll1 is offline  
Old 24th Jul 2019, 11:12 pm   #49
emeritus
Dekatron
 
Join Date: Jan 2012
Location: Brentwood, Essex, UK.
Posts: 5,337
Default Re: Isolation/isolating transformers

Interesting use of a train controller. I suppose it would have been for something like the Lionel O gauge system and would have been capable of delivering a couple of amps at up to 20V.
emeritus is offline  
Old 5th Aug 2019, 7:05 pm   #50
6.3volts
Pentode
 
6.3volts's Avatar
 
Join Date: Nov 2009
Location: Welshpool, Powys, UK.
Posts: 121
Default Re: Isolation/isolating transformers

This may cause a few raised eybrows but I went down the route of two 110V equipment transformers back to back to give 240 and 110 both isolated from the grid and each other. Tons of power with no sag and about £100 spend.
6.3volts is offline  
Closed Thread

Thread Tools



All times are GMT +1. The time now is 12:22 pm.


All information and advice on this forum is subject to the WARNING AND DISCLAIMER located at https://www.vintage-radio.net/rules.html.
Failure to heed this warning may result in death or serious injury to yourself and/or others.


Powered by vBulletin®
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright ©2002 - 2023, Paul Stenning.