19th Nov 2018, 10:58 pm | #21 |
Dekatron
Join Date: Apr 2005
Location: North Wales, UK.
Posts: 6,925
|
Re: Neon tester vs dodgy wiring
Thanks for all the comments. I always used the abbreviation RCCB - must be getting old! The consumer unit is quite old as well, though, with just four MCBs (one unused).
My partner did suggest replacing the switches with plastic ones, but my point is that the fault wouldn't be cured, and also the metal screws would also be live, so someone coming in from the outside with wet feet (which is beside one affected switch) could easily come into contact with it. I doubt RF is to blame as it seems odd that only certain plates are affected - and there's still an earth fault present even if that were the case. I did isolate each switch in case one was leaking, but the earth conductor is carrying the voltage. I suspect post #8 may be close to the truth as I used a digital meter, but as he says there is still an earth fault. Also post#4 - there IS a smell of urine about.... The owners have agreed to get an electrician in to inspect so hopefully all will be revealed. I'll update the post as it is of interest. |
19th Nov 2018, 11:55 pm | #22 |
Dekatron
Join Date: Aug 2016
Location: Colchester, Essex, UK.
Posts: 4,108
|
Re: Neon tester vs dodgy wiring
Please do, you have our attention now..
As you said it's all cross bonded- wonder if it's something as simple as a dead rat in the loft draped over a junction box. Dave |
19th Nov 2018, 11:59 pm | #23 |
Hexode
Join Date: Jan 2012
Location: Weymouth, Dorset, UK.
Posts: 422
|
Re: Neon tester vs dodgy wiring
I think it's good that an electrician is going to have a look at it all 10mA could be dangerous especially if the person is not in good health. Finally I think it probably is switch leakage replacing them with plastic ones would fix it. Finally is the place damp? That might be part of the issue.
|
20th Nov 2018, 12:12 am | #24 |
Nonode
Join Date: Jun 2007
Location: Coulsdon, London, UK.
Posts: 2,167
|
Re: Neon tester vs dodgy wiring
The 'wet' areas such as bathroom and kitchen need to be checked carefully, especially any exposed metalwork.
|
20th Nov 2018, 12:32 am | #25 |
Dekatron
Join Date: May 2010
Location: Greater Manchester, UK.
Posts: 18,723
|
Re: Neon tester vs dodgy wiring
Glyn, If the room has been wallpapered perhaps damp wallpaper has been slipped behind the switch-plates creating electrical leakage to the un-earthed metalwork?
__________________
-- Graham. G3ZVT |
20th Nov 2018, 10:27 am | #26 | |
Rest in Peace
Join Date: Mar 2011
Location: Basildon, Essex, UK.
Posts: 4,100
|
Re: Neon tester vs dodgy wiring
Quote:
The back box and face plate need to be earthed. Mike |
|
20th Nov 2018, 10:31 am | #27 |
Dekatron
Join Date: Aug 2016
Location: Colchester, Essex, UK.
Posts: 4,108
|
Re: Neon tester vs dodgy wiring
If i have read this right, Glyn isolated each switch plate from the earth wire and found that the juice was coming from the earth wire.
Dave |
20th Nov 2018, 12:17 pm | #28 |
Dekatron
Join Date: Feb 2007
Location: Leominster, Herefordshire, UK.
Posts: 16,536
|
Re: Neon tester vs dodgy wiring
Which is well and truly dodgy
Let's see if the sparky finds anything exciting......
__________________
....__________ ....|____||__|__\_____ .=.| _---\__|__|_---_|. .........O..Chris....O |
20th Nov 2018, 1:51 pm | #29 |
Octode
Join Date: Jan 2012
Location: Wimbledon, London, UK.
Posts: 1,465
|
Re: Neon tester vs dodgy wiring
I came across a similar problem a few years ago when I was re-decorating a bathroom in a flat. I found that a wall-mounted radiant electric heater had full mains voltage on its (supposedly earthed) metal casing. After chasing around pulling up floorboards and the like, I found that some expensive metal double socket outlets were live and that the lighting circuit and one of the ring-mains had their lines connected. I eventually found a nail which had been driven into the wall to hang a picture had 250 V on it. This nail had blown a piece of the earth conductor in the twin-and-earth wiring and had also shorted between the line of the ring-main and that of the lighting circuit. I eventually dug out the wiring that was embedded in the plaster and replaced it. I understood at the time that a previous owner was an electrician and had installed all of the expensive metal double sockets. What a pity he didn't put a blanking-plate on the pattress where I found the melted earth-wire, rather than just wallpapering over it!
Colin. |
20th Nov 2018, 3:57 pm | #30 |
Hexode
Join Date: Dec 2006
Location: Norwich, Norfolk, UK.
Posts: 440
|
Re: Neon tester vs dodgy wiring
Loose or disconnected neutral on the consumer side of the meter?
|
20th Nov 2018, 8:24 pm | #31 |
Hexode
Join Date: Jan 2012
Location: Weymouth, Dorset, UK.
Posts: 422
|
Re: Neon tester vs dodgy wiring
Colin.
Many years ago I lived in a bungalow and my dad put a nail in the wall to hang a photo on. Afterwards we found the bath was slightly live, you could get a distinct tingle with one foot in the bath and the other on the cement floor. The fault was really as you described the nail grazed the live wire and was also in contact with the lead sheath. We got a local electrician to sort it out. |
20th Nov 2018, 9:57 pm | #32 |
Heptode
Join Date: Dec 2010
Location: Barnstaple, N.Devon, UK.
Posts: 557
|
Re: Neon tester vs dodgy wiring
Hi again, Re post 26/27, I had thought he meant the switch plate was leaking when not connected to earth.
Sorry, my mistake. As I said though, it's impossible to know without being there to do some tests and inspection. When I moved to my current address (no pun intended), I found I got a tingle from the dinning room light fitting whether switched on or off. When I got round to taking it down, there were a collection of choc blocks behind, and where you would expect 4 terminals, L,N,E and switch return, there were in fact five. Whoever changed the light fitting had connected the mains earth and loop through earth together and then the switch earth and light fitting earth together in a seperate terminal ! I won't go in to the other things I have since discovered, one being a piece of 3 core rubber flex from the fuse box to feed 10 different lights (and it's an old colours piece of flex) 2.5mm used for lighting etc. It's worrying when you think these sort of things would be checked before a property goes on the market but I've seen many things that would not pass a proper inspection. One thing to note in Glyn's original post is the existence of rubber cable in the installation. In lighting circuits old enough to have been made in rubber there was quite often no earth at all. Maybe there is no earth feeding the lighting circuit but later fittings and switches have been wired in twin and earth. Then it's going to be leakage through the capacitance of the cables. I do hope Glyn comes back with some news. David. |
20th Nov 2018, 10:45 pm | #33 |
Hexode
Join Date: Oct 2012
Location: London, UK.
Posts: 498
|
Re: Neon tester vs dodgy wiring
|
21st Nov 2018, 10:55 am | #34 |
Dekatron
Join Date: Apr 2005
Location: North Wales, UK.
Posts: 6,925
|
Re: Neon tester vs dodgy wiring
Or Wales!
I've contacted the owners and they are sending their electrician. Mind you, if he's the one that's done the work I won't be too confident. Ref post #32 there is one twin and earth from the consumer unit feeding all the lighting. This earth is good and there is good continuity from this and all other parts of the house to exposed metalwork (all X-bonded). I suspect whoever connected the lower floor just found live and neutral in a lighting junction box and connected the circuit to that. However, I would have thought all the earths would have been connected together somewhere, but that doesn't seem to be the case. Odd! I've checked for dampness, mails and so on. I'm just going to have a look at an outside light. I'll keep you posted! Last edited by Welsh Anorak; 21st Nov 2018 at 11:07 am. |
21st Nov 2018, 11:40 am | #35 | |
Moderator
Join Date: Jun 2003
Location: Oxford, UK
Posts: 27,960
|
Re: Neon tester vs dodgy wiring
Quote:
|
|
21st Nov 2018, 12:01 pm | #36 |
Dekatron
Join Date: Aug 2016
Location: Colchester, Essex, UK.
Posts: 4,108
|
Re: Neon tester vs dodgy wiring
Ah, outside lights. Seems whether IP44, IP65, sooner or later the water gets in and stays in. Just bought an LED luminaire but protecting it with a metal hood as the cable entry gland faces upwards with the light shining downwards.
Dave |
21st Nov 2018, 12:46 pm | #37 | |
Heptode
Join Date: May 2009
Location: Birmingham, West Midlands, UK.
Posts: 708
|
Re: Neon tester vs dodgy wiring
Quote:
(if you have now earthed the backboxes and the symptoms remain then don't bother with the following) If it's an older property then the backboxes are often cemented into the brickwork, these sometimes corrode at the back obviously due to the reaction of the cement and any moisture in the walls, the backbox thus becomes a capacitor plate with a charge...don't laugh. PS. electricians often leave these old boxes in because they can be absolute hell to get out..much chiseling and damage to brickwork as well. Last edited by cheerfulcharlie; 21st Nov 2018 at 12:52 pm. |
|
21st Nov 2018, 1:43 pm | #38 |
Dekatron
Join Date: Aug 2016
Location: Colchester, Essex, UK.
Posts: 4,108
|
Re: Neon tester vs dodgy wiring
I can well believe this sort of electrolytic weirdness...would it be DC in this scenario?
Dave |
21st Nov 2018, 5:00 pm | #39 | |
Dekatron
Join Date: Nov 2003
Location: Heckmondwike, West Yorkshire, UK.
Posts: 9,642
|
Re: Neon tester vs dodgy wiring
Quote:
Whatever your opinion of them, they're deemed competent by whoever and will be responsible for any consequences. |
|
21st Nov 2018, 6:27 pm | #40 | ||
Nonode
Join Date: Jan 2016
Location: Stafford, Staffs. UK.
Posts: 2,532
|
Re: Neon tester vs dodgy wiring
Quote:
Quote:
|
||