3rd Nov 2010, 8:43 pm | #21 | |
Dekatron
Join Date: Jun 2005
Location: Warnham, West Sussex. 10 miles south of DORKING.
Posts: 9,147
|
Re: National grid frequency
Quote:
It still has its original box. No idea of it's age. J |
|
3rd Nov 2010, 9:11 pm | #22 |
Dekatron
Join Date: Feb 2005
Location: St.Ippolyts, Hitchin, Hertfordshire QRA IO91UW
Posts: 3,518
|
Re: National grid frequency
Er yes, synching a generator out of phase is a very bad thing, and does give a loud bang!
Think of trying to stop your car engine by throwing a steel bar through the flywheel..... The peak current is quite impressive - certainly enough to phisically lift several tons of alternator.....
__________________
Engineers make things work and have spare bits when finished |
3rd Nov 2010, 9:50 pm | #23 |
Rest in Peace
Join Date: Dec 2008
Location: Burton upon Trent, East Staffordshire, UK.
Posts: 1,686
|
Re: National grid frequency
When I was at college we carried out just such an experiment. We had to synchrinise a local motor/generator set to the incoming three phase and then put a plug into a set of sockets to connect them together. We were then meant to vary the phase difference and observe the current flows. My 'colleague' got the wrong end of the stick and banged the plug in when they weren't properly phased. It took out every breaker in the Lab block.
Still, we got off early Alan |
3rd Nov 2010, 11:42 pm | #24 | |
Dekatron
Join Date: Jul 2007
Location: Penrith, Cumbria, UK.
Posts: 3,687
|
Re: National grid frequency
Quote:
I have synchronised alternators (and a humungous synchronous motor) in the past with the aid of a synchroscope and 'lamps, dim' (as opposed to 'lamps, bright' - another method), although the generators I deal with nowadays are auto-synching and autonomous: not parallelled with the grid!
__________________
Regds, Russell W. B. G4YLI. |
|
3rd Nov 2010, 11:58 pm | #25 |
Rest in Peace
Join Date: Dec 2008
Location: Burton upon Trent, East Staffordshire, UK.
Posts: 1,686
|
Re: National grid frequency
Russell,
Some of it comes back to me. I think that's where he got it wrong Alan |
4th Nov 2010, 8:11 am | #26 |
Retired Dormant Member
Join Date: Dec 2003
Location: North London, UK.
Posts: 6,168
|
Re: National grid frequency
Sounds familiar. In Eric Laithwaite's lab at Imperial College we did something very similar, using an antiquated 3 lamp synchroniser. One group (not mine!) got it 180 out and blew the lab fuses. Even a few degrees out will make the alternator complain as a large rotating lump of metal tries to move instantly to a different angle.
|
4th Nov 2010, 9:40 am | #27 | |
Octode
Join Date: Jan 2004
Location: Southport, Merseyside, UK.
Posts: 1,156
|
Re: National grid frequency
Quote:
John |
|
4th Nov 2010, 10:04 am | #28 |
Retired Dormant Member
Join Date: Oct 2010
Location: Colne, Lancashire, UK.
Posts: 527
|
Re: National grid frequency
One of these things? I want one...
|
4th Nov 2010, 10:07 am | #29 |
Octode
Join Date: Apr 2009
Location: Aylesbury, Buckinghamshire, UK.
Posts: 1,522
|
Re: National grid frequency
I was working on some generators a while ago that had RCD's fitted as an after thought. When the RCD was reset, it threw the contactor straight in without Syncing up first, quite scary to see several tonne of machinery jump six inches across the yard.
I still think it's wonderful that by varying the excitation you can make an alternator act like a capacitor or inductor. Rob.
__________________
We have done so much, for so long, with so little, we are now qualified to do anything with nothing. |
4th Nov 2010, 1:49 pm | #30 |
Dekatron
Join Date: Feb 2007
Location: Lynton, N. Devon, UK.
Posts: 7,088
|
Re: National grid frequency
When syncing an incoming generator to an established supply, using a synchroniser or the lamp method, is it not possible to connect via low-value resistors which are then switched out of circuit? The incoming generator will then be pulled gently into full sync. Afterwards, the excitation can be fine-adjusted to set the load.
The resistors would only take a hammering if sync was significantly out. And in this case, a bank of sacrificial resistors would be much cheaper and quicker to replace than a wrecked alternator. |
4th Nov 2010, 1:53 pm | #31 |
Dekatron
Join Date: Jul 2007
Location: Penrith, Cumbria, UK.
Posts: 3,687
|
Re: National grid frequency
Nearly... It was much older than that, and circular.
__________________
Regds, Russell W. B. G4YLI. |
4th Nov 2010, 2:19 pm | #32 |
Rest in Peace
Join Date: Sep 2008
Location: Solihull, West Midlands, UK.
Posts: 4,872
|
Re: National grid frequency
I think a series resistor for syncing would need to be rather large (a few MW?), even though the generator excitation would presumably be set for low power until synced. Someone who was likely to wreck a generator would not be set loose on a unit desk!
|
4th Nov 2010, 4:41 pm | #33 |
Octode
Join Date: Apr 2009
Location: Aylesbury, Buckinghamshire, UK.
Posts: 1,522
|
Re: National grid frequency
Not really required if syncing is carried out properly. If anything you want the generator coming on stream to be running slightly faster than synchronous speed to prevent reverse power. The excitation is adjusted to give the same voltage as that on the bus before syncing, once synced it is adjusted to give equal power factor on all sets. The "throttle" is then opened to load up the set (with real power).
Rob.
__________________
We have done so much, for so long, with so little, we are now qualified to do anything with nothing. |
4th Nov 2010, 11:53 pm | #34 |
Heptode
Join Date: Jun 2006
Location: Milton Keynes, Buckinghamshire, UK.
Posts: 931
|
Re: National grid frequency
Ah, "twanger" meters! I've got one of them rattling around somewhere - unfortunately it's 115V and 60Hz though!
Was going to dig it out and snap a photo of it - until I realised how deeply buried in the wardrobe it is...can wait till the weekend! It's really interesting though actually being able to see the grid's behaviour in real time though. |
5th Nov 2010, 2:04 pm | #35 |
Rest in Peace
Join Date: Apr 2008
Location: London, UK.
Posts: 2,508
|
Re: National grid frequency
Anybody who like fidding with big alternators etc should be well at home at Electrokinetica once we're up and running. In fact one of the interactive demo's that I've been pondering about setting up is a fool-proof real-time demonstration of the process, that people can experiment with by following the instructions and prompts from the (hidden) controller. Not a mock-up though - a running generator delivering real power to the museum mains.
It's something for the tech heads to get to grips with while the rest of the family are comparing vacuum cleaners and playing 70's video games! Lucien |
5th Nov 2010, 3:09 pm | #36 |
Retired Dormant Member
Join Date: Oct 2010
Location: Colne, Lancashire, UK.
Posts: 527
|
Re: National grid frequency
|
5th Nov 2010, 3:31 pm | #37 |
Dekatron
Join Date: Mar 2008
Location: St. Frajou, l'Isle en Dodon, Haute Garonne, France.(Previously: Ellesmere Port, Cheshire, UK.)
Posts: 3,184
|
Re: National grid frequency
Hi,
In reply to G8HQP Dave's reply, synchronising an alternator when the excitation is weak runs the risk of "pole slipping" when the grid can pull an alternator out of synch a phase at a time instead of in. I've never witnessed it at the stations I worked at, but the engineers reckon it can be almost as spectacular as not synching properly in the first place. One day we had a 500MW unit trip which took us off the bars & shut the steam off to the turbine - but - the breaker feeding the station supplies didn't trip and for a few seconds the whole station slowed down as the alternator ran down while still generating. I was in the auxiliary boilerhouse at the time and it was a strange experience watching (and hearing) all the motors slowly grind to a halt followed by an eerie silence before the panic set in. Sorry if I've de-synched the thread Cheers, Pete
__________________
"Hello?, Yes, I'm on the train, I might lose the signal soon as we're just going into a tunn..." |
5th Nov 2010, 4:45 pm | #38 |
Dekatron
Join Date: Feb 2007
Location: Lynton, N. Devon, UK.
Posts: 7,088
|
Re: National grid frequency
Some years back, during a bad winter with power cables down, Lynton was running from its local standby generator (gas turbine based - off grid) which ran out of fuel. All lights everywhere dimmed out to blackness over about 10 seconds.
It would have been great to have been watching the frequency, or the mains waveform, at the time - obviously with independently powered equipment |