Old 2nd Sep 2015, 5:55 pm   #1
Sparky67
Heptode
 
Sparky67's Avatar
 
Join Date: Feb 2008
Location: Great Barr, Sandwell, West Midlands, UK.
Posts: 589
Default Lightning and Antennas

I live in a house on a hill, with antennas on the roof. 20 years ago we were struck by lightning - a side fork I believe - which destroyed most of the electrical equipment in the house including my amateur radio station. The smell of burning at 2am and finding none of the lights work, with two small children in the house, isn't something I would recommend.

The question is - do I disconnect all antennas when there is lightning about or do I fit an earthing system to the antennas and leave them connected? At the moment I disconnect the antennas and unplug everything from the mains to try to prevent a leader developing. Your thoughts?
Sparky67 is offline  
Old 2nd Sep 2015, 7:02 pm   #2
kellys_eye
Octode
 
Join Date: Jan 2014
Location: Oban, Scotland, UK.
Posts: 1,129
Default Re: Lightning and Antennas

Usual practise was to leave the aerial open circuit and earth the receiver input. The idea being that lightning finds the shortest route to earth and if the aerial is 'floating' there's less chance of it attraccting a strike.

I suspect that nothing will prevent a direct lightning strike causing major damage though.
kellys_eye is offline  
Old 2nd Sep 2015, 7:02 pm   #3
Radio Wrangler
Moderator
 
Radio Wrangler's Avatar
 
Join Date: Mar 2012
Location: Fife, Scotland, UK.
Posts: 22,902
Default Re: Lightning and Antennas

One school of thought is that you have the antennae earthed, but do it outside the house, to a proper earth rod, then if the worst happens, there is a degree of isolation.

The idea is that spiky things are supposed to spray appropriate charges, discharging the air around them. Lightning conductors are really lightning preventers and have a sort of conical volume underneath them which is considered to be protected.

David
__________________
Can't afford the volcanic island yet, but the plans for my monorail and the goons' uniforms are done
Radio Wrangler is online now  
Old 2nd Sep 2015, 7:29 pm   #4
G6Tanuki
Dekatron
 
G6Tanuki's Avatar
 
Join Date: Apr 2012
Location: Wiltshire, UK.
Posts: 14,007
Default Re: Lightning and Antennas

I recall seeing in some photos of pre-WWII amateur stations a big knife-switch used to earth the aerial when it wasn't in use.

You can buy 'in-line' coaxial lightning-protectors with SO239 sockets and a nut/bolt for attaching an earth-wire. To use one of these with a traditional wire antenna - remember that 4mm banana-plugs fit SO239 sockets!

http://www.hamradio.com/detail.cfm?pid=H0-006891 [MFJ stuff is available from plenty of UK ham-radio resellers too].

When I was running HF backbone links the standard inline thingy was a Polyphaser: http://www.dxengineering.com/search/...ing-protectors

Though if you get a direct hit then nothing much will save you [your flexible coax cable can go solid when the individual strands of the braid weld to each other...]
G6Tanuki is offline  
Old 3rd Sep 2015, 3:06 am   #5
Refugee
Dekatron
 
Refugee's Avatar
 
Join Date: Apr 2012
Location: Worksop, Nottinghamshire, UK.
Posts: 5,554
Default Re: Lightning and Antennas

I was told that when my father was very young their house got struck and the lightning just jumped from the end of the aerial wire to the radio and did the damage anyway.
Outside it blew the chimney stack off sending it into an upstairs room in the house next door.
Refugee is offline  
Old 3rd Sep 2015, 5:59 am   #6
Billy T
Retired Dormant Member
 
Join Date: Feb 2008
Location: Auckland, New Zealand
Posts: 631
Exclamation Re: Lightning and Antennas

.
Most lightning damage is caused by induced voltages and currents, so disconnection/grounding etc can be an effective precaution to minimise such collateral damage in some cases.

However, the discharge current of a true 'strike' knows no barriers and will wreak havoc regardless of any and all 'domestic grade' precautions, and most commercial protections as well. In fact, it is arguable that lightning protection apropo domestic installations is a waste of time and it is better to simply disconnect any sensitive equipment and wait for the storm to pass.

Look up 'lightning strike damage' in 'Google Images' and you will see just how impotent any precautions taken may be, should nature decide to bite!

A few years back I was working overseas doing risk assessment on government buildings of a Commonwealth country and in the multistorey building housing their computer systems I saw that their lightning conductor was run from roof to basement inside a steel waterpipe. Following that pipe up to the roof, I then found that the lightning rod itself had suffered physical damage at some time and had been removed, so the connection had bee attached to a metal ventilator shaft. The site was in a known electrical storm area, so I advised that they begin an urgent review of the entire system and get started on a remedial program.

A few months of inaction later, they were hit by a major electrical storm and immense damage was done to their electrical and computer networks*. All that the pipe did was channel the strike energy down several floors to the server room, blowing out electrical/electonic systems on every floor as it went.


'Switch off, unplug and disconnect' is by far the best precaution you can take, and that should be done before the thunder rumbles, that is what weather forecasts are for. Bear in mind that a 'leader' usually goes up before the 'strike' comes down, hence 'hair standing on end' etc.

Billy

*As a final insult, the batteries for their extensive UPS systems were knackered as well, so their UPS had a run-time only slightly longer than the lightning strike.
Billy T is offline  
Old 3rd Sep 2015, 8:19 am   #7
Radio Wrangler
Moderator
 
Radio Wrangler's Avatar
 
Join Date: Mar 2012
Location: Fife, Scotland, UK.
Posts: 22,902
Default Re: Lightning and Antennas

Lightning effects on ground installations have been studied, but not to the extent those on aircraft have.

Aircraft get struck by lightning relatively frequently. An arc attaches somewhere to the fuselage, current flows through the fuselage and an arc towards the ground starts from somewhere else. Usually pointy things are preferential attachment points - radio antennae!
Planes have static discharge wicks deigned to minimise the build-up of potential so landings aren't accompanied with huge zaps. The wicks are likely continuation arc points. Effectively the plane becomes a series connection along the path of a lightning strike.

A direct hit can melt antenna elements and cables. he hope is that the backup radio isn't damaged by the induced surge.

The strike passes a huge current through a metal plane. The evolution towards carbon fibre aeroplanes has a nasty consequence that the planes are becoming much higher resistance and the amount of energy dissipated along the current flow route increases massively., threatening major structural damage. Airframe manufacturers are having to incorporate metal mesh layers to restore protection.

There's been a lot of work done on lightning effects and there is a standards document setting out what performance a good radio (and other systems) installation must have and how to test it.

DO-160G is the latest revision. Chapter 22 covers the effects of direct lightning hits. Chapter 23 covers induced transients applied to radios when other parts are struck.

The direct stuff doesn't help us much down on the ground except for people living in fully enclosing all-steel houses (There are some of those in Kirkliston, built from recycled ship's plates!) But the indirect induced effects are a good guide.

Differential potentials on a struck airframe are expected to couple up to 125v/125A surges with a 40us rise time (0 to 100%) and then to fall with an 80us (100 to 50%) exponential decay. This can be positive or negative going. Apply this to every pin of every connector in both polarities.

Induction from the current path/wiring is expected to apply a damped sine ring to each connection to a radio. 250v/10A peak, both starting polarities. 1MHz for longer wires in large planes, 10MHz for small planes to represent typical resonant frequencies.

How do you protect against these? Well you certainly need to make sure no connection presents an impedance close to 1 Ohm, that'll match it to the 125V/125A transient, and it'll hit a peak power of 3.9 kilowatts! Ouch! The ring waveform only peaks at 600+ watts.

There are whacking great (by modern standards) Zener diodes called TVS diodes. The big 'SMC' sized ones will handle 1200W peak and routinely survive the tests when placed right at the input of a connection. If your connection can tolerate several tens of Ohms series resistor right at the connector, you can use smaller SMB or even SMA (no, not the connector) sized diodes.

The Apple MAC I'm typing this on had a blown-up ethernet port. Apple say it's £600 for a new motherboard. It looks like an antenna flashover dnced around the shack while I was away last year. An ethernet to 'thunderbolt port' adapter is an amusingly ironic cure which cost an awful lot less.

Grounding things in domestic radio installations runs into a whole lot of regulatory pain over PME earthing schemes.

David
__________________
Can't afford the volcanic island yet, but the plans for my monorail and the goons' uniforms are done
Radio Wrangler is online now  
Old 3rd Sep 2015, 9:48 am   #8
G4_Pete
Hexode
 
Join Date: Feb 2014
Location: Southampton, Hampshire, UK.
Posts: 419
Default Re: Lightning and Antennas

Whilst it may detract from the hobby and the feel of being able to adjust tuning ect the only low risk way if you are in a high probability lightening site is to put all the radio gear in a remote shed and fibre optic back to your house. In industry this is how we brought critical computer lines back in to the control houses. Everything else cabled came into the building via a huge earthed plate on the outside wall with appropriate earthing and lightening traps depending on the cable service. Secondary transient protection or earthing was then applied on signal lines as apropriate.

Unplugging cables on a storm approach is not without risk as potentials build up in the air prior to a full blown storm and you do not want to be holding the cable in one hand in this situation. I have had sparks jumping between the centre and braid on a sloping dipole with what I thought was a distant storm aproach.
Pete
G4_Pete is offline  
Old 3rd Sep 2015, 10:08 am   #9
lesmw0sec
Octode
 
Join Date: Jul 2009
Location: Carmel, Llannerchymedd, Anglesey, UK.
Posts: 1,509
Default Re: Lightning and Antennas

It is always worth unplugging aerials when not in use. Here on Anglesey we often get a sudden increase in static with no warning and in the absence of a storm. I had to replace the bulb 'fuse' in an FT101 as a result of leaving a 160M dipole plugged in. Fortunately the fuse did its job well.
lesmw0sec is offline  
Old 3rd Sep 2015, 2:08 pm   #10
G6Tanuki
Dekatron
 
G6Tanuki's Avatar
 
Join Date: Apr 2012
Location: Wiltshire, UK.
Posts: 14,007
Default Re: Lightning and Antennas

Quote:
Originally Posted by G4_Pete View Post
Everything else cabled came into the building via a huge earthed plate on the outside wall with appropriate earthing and lightening traps depending on the cable service.
That's the technique known as "ground windowing" - see para.8 of http://lightning-protection-institut...ng-protect.htm
G6Tanuki is offline  
Old 3rd Sep 2015, 5:10 pm   #11
paulsherwin
Moderator
 
paulsherwin's Avatar
 
Join Date: Jun 2003
Location: Oxford, UK
Posts: 27,970
Default Re: Lightning and Antennas

Before the 1960s most UK households had big professionally installed longwire aerials stretching across the garden or back yard. These were usually terminated by a substantial knife switch on the windowsill where the aerial entered the house, allowing easy isolation once the thunder started or when the radio wasn't in use.
paulsherwin is offline  
Old 3rd Sep 2015, 6:45 pm   #12
emeritus
Dekatron
 
Join Date: Jan 2012
Location: Brentwood, Essex, UK.
Posts: 5,349
Default Re: Lightning and Antennas

Interestingly enough, the 1936-37 Bulgin catalogue does not offer a substantial knife switch, but a compact "QMB Lightning Switch and Arrester", the effectiveness of which they were sufficiently confident to offer a "£100 guarantee of efficiency". I wonder if anyone ever made a claim? PDFs of the catalogue extract and the patent covering the switch attached.
Attached Files
File Type: pdf Bulgin lightning arresters 1936_7.pdf (159.9 KB, 127 views)
File Type: pdf GB000000394805A_all.pdf (1.78 MB, 90 views)
emeritus is offline  
Old 3rd Sep 2015, 7:59 pm   #13
russell_w_b
Dekatron
 
russell_w_b's Avatar
 
Join Date: Jul 2007
Location: Penrith, Cumbria, UK.
Posts: 3,687
Default Re: Lightning and Antennas

I guess if your AMU is configured with an inductor to earth at the aerial side or shunt loading coil arrangement you'd have a static leak to prevent a charge building up (but not a direct strike). Or perhaps you could connect a hi-Z choke to the aerial as a permanent static leak?
__________________
Regds,

Russell W. B.
G4YLI.
russell_w_b is offline  
Old 19th Sep 2015, 9:57 am   #14
Sparky67
Heptode
 
Sparky67's Avatar
 
Join Date: Feb 2008
Location: Great Barr, Sandwell, West Midlands, UK.
Posts: 589
Default Re: Lightning and Antennas

Thanks for the advice chaps. In a previous life I installed antenna systems on towers and have removed large antennas which have been struck by lightning several times - the damage to the finials was obvious - although no damage inside the building occurred (except one site where the BT line terminations got fried...!). On these sites the feeder braids were earthed at the top and bottom of the tower and just before the building ingress. The radio eqpt chassis were connected to their racks, the racks were bonded back to the tower (via 25x3mm tape) and the tower legs were cross-bonded and the whole system had a <15 Ohms resistance to earth. I was told the cross-bonding kept everything 'earthed' at the same potential during a strike and prevented damage.

I suspect to fully protect the radio station in the house would require a lot of earth tape, earth rods and cross-bonding. Think disconnecting and crossing fingers is going to be the way forwards for me...
Sparky67 is offline  
Old 19th Sep 2015, 5:02 pm   #15
G6Tanuki
Dekatron
 
G6Tanuki's Avatar
 
Join Date: Apr 2012
Location: Wiltshire, UK.
Posts: 14,007
Default Re: Lightning and Antennas

You were lucky: one lightning-strike I had to deal with welded the sections of a 60-foot trailer-mount telescopic "Versatower" together. The strike also catastrophically melted the winch-cable. When I got to the site the mast was half-telescoped-down and firmly stuck like that, going nowhere.

The wheel-bearings on the trailer were also welded solid! We cut the lot up on-site using angle-grinders and oxy-acetylene, cashed it in as scrap, and claimed on the insurance.
G6Tanuki is offline  
Old 19th Sep 2015, 11:01 pm   #16
peter.sables
Rest in Peace
 
peter.sables's Avatar
 
Join Date: Dec 2007
Location: Doncaster, South Yorkshire, UK.
Posts: 385
Default Re: Lightning and Antennas

In the Army serving in Malaya. We had lots and lots of ground strikes. We saved the coax and set by this little tabaco tin. Simple but it worked (most of the time.

Pete G4MRU
Attached Thumbnails
Click image for larger version

Name:	lighting stike.jpg
Views:	344
Size:	30.1 KB
ID:	113251  
peter.sables is offline  
Old 1st Oct 2015, 9:10 pm   #17
QWENIX
Pentode
 
QWENIX's Avatar
 
Join Date: Jan 2006
Location: Amsterdam, The Netherlands
Posts: 180
Default Re: Lightning and Antennas

Never ever connect the antenna to earth. Leave the circuit open. It's wise to extra discharge the antenna after the lightning weather has gone. So no built up voltage charge could damage the equipment by discharging through the equipment to earth. Only the mast could use a lightning conductor.

qwenix
QWENIX is offline  
Old 1st Oct 2015, 10:11 pm   #18
peter.sables
Rest in Peace
 
peter.sables's Avatar
 
Join Date: Dec 2007
Location: Doncaster, South Yorkshire, UK.
Posts: 385
Default Re: Lightning and Antennas

Hi.
I think maybe you have missed the point. The shellac is covering the bearing So the antenna is not earthed. The shellac is regarded as one micron thick at the top of the bearing. So the antenna is not earthed. But the smallest heat will short out the antenna very quickly. Maybe a little "heath Robinson". The bottom of the bearing has no shellac on it. ie earthed. We also had a flat carbon block, once again with shellac covering one face of it.

Pete
peter.sables is offline  
Old 1st Oct 2015, 11:48 pm   #19
Peter.N.
Dekatron
 
Join Date: Jul 2008
Location: Charmouth, Dorset, UK.
Posts: 3,601
Default Re: Lightning and Antennas

I'm afraid I do nothing with my ham antennas, I don't even have an earth in the shack as my only HF aerial at present is a 200' balanced fed dipole which I can tune up on any band, my 2m ant is at about 40' and we are 500'ASL.

I was looking out of the window during one storm and the 11kv power line was struck about 2 poles down the hill from us which must be at least 50' lower. I did have my router blown up by a strike but that was further down the road.

Peter
Peter.N. is offline  
Closed Thread




All times are GMT +1. The time now is 3:02 am.


All information and advice on this forum is subject to the WARNING AND DISCLAIMER located at https://www.vintage-radio.net/rules.html.
Failure to heed this warning may result in death or serious injury to yourself and/or others.


Powered by vBulletin®
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright ©2002 - 2023, Paul Stenning.