Vintage Amateur and Military Radio Amateur/military receivers and transmitters, morse, and any other related vintage comms equipment. |
|
Thread Tools |
20th Jul 2008, 7:00 pm | #21 | |
Dekatron
Join Date: Jul 2007
Location: Penrith, Cumbria, UK.
Posts: 3,687
|
Re: PME and RF Galvanic Isolation
Quote:
David, Many thanks for answering my question! I understand that cattle are indeed sensitive to potential gradient. Better get back on topic now, I suppose...
__________________
Regds, Russell W. B. G4YLI. |
|
20th Jul 2008, 9:53 pm | #22 | |
Rest in Peace
Join Date: Jun 2006
Location: Chard, South Somerset, UK.
Posts: 7,457
|
Re: PME and RF Galvanic Isolation
Quote:
Picking up on that - and John Robson's Post - surely the whole idea of running an earth wire into a domestic installation is simply a safety feature - almost along the lines that John R stated. One side of the incoming mains is at earth at the substation. Should the line / "live" wire in a piece of equipment contact its earthed metal casing, it will simply blow a fuse / trip the RCD - and save the user from electrocution - who will be in physical contact (or nearly so) with "earth". If the incoming mains was balanced to earth and there were not any earth connections anywhere on the load side of the sub-station transformer, an earth lead would not be required - which, in essence, is the result when an isolating transformer is used in a domestic installation to power various item(s) that the consumer chooses to so connect. In which case, the question arises: why does the secondary side on the transformer at the sub-station have one side of its winding connected to earth anyway? Why not simply run 4-wire balanced 415v a.c. line-line 3-phase to consumer installations, producing 2-wire 230v a.c. phase - neutral balanced feeds? I'm sure you'll educate me on these points - thank you. Al / Skywave. |
|
20th Jul 2008, 10:45 pm | #23 | |
Dekatron
Join Date: Jul 2007
Location: Penrith, Cumbria, UK.
Posts: 3,687
|
Re: PME and RF Galvanic Isolation
Quote:
Well, if the incoming mains was balanced (ie: no particular phase was neutral), then a faulty appliance with a wire touching the case would go un-noticed by whoever was touching it - until they touched (or the faulty metallic case of the appliance touched) another piece of faulty equipment with a wire from the other phase touching its case! This is why it's not good practise to connect a multiway extension block to one of these little generators with floating supplies. Faulty appliances go un-noticed until someone picks up two faulty appliances on the extension block; one with a live-to-earth fault and the other with neutral-to-earth fault - Arghhh! Similarly, if one wire of a balanced system supply made inadvertent and unbeknownst contact with earth, then the system becomes unbalanced and provides a path from the phase in the faulty appliance, through the unfortunate person holding it, through earth, and back to the other phase through the inadvertent and unbeknownst supply earth fault. If one phase is solidly referenced to earth, the above won't happen (assuming they're wired correctly, of course!).
__________________
Regds, Russell W. B. G4YLI. |
|
21st Jul 2008, 12:04 am | #24 |
Rest in Peace
Join Date: Jun 2006
Location: Chard, South Somerset, UK.
Posts: 7,457
|
Re: PME and RF Galvanic Isolation
Thanks Russell.
As you've probably guessed - I hadn't thought of those scenarios that you so lucidly explain. Also, I now stand educated on why it is not a good idea to run more than one item from a mains-powered isolation transformer - unless all items are in metal cases and the metal cases are substantially bonded together (this becomes clear in a quick drawing). Incidentally, I was thinking of star-connected secondaries at the sub-station without a connection from the star point to earth - viz. a truly floating neutral - but your reasoning covers that situation also. Al / Skywave. |
22nd Jul 2008, 12:09 pm | #25 |
Nonode
Join Date: Mar 2008
Location: Aberdeen, UK.
Posts: 2,857
|
Re: PME and RF Galvanic Isolation
Guys, Have consulted an ex BT Telecomms Station Manager. Refering to the days before satelite & microwave parabolic antennas, all HF & VHF stations had 3 "Earths" :- 1) Electricity Supplier's Earth - for all building's ring mains, lighting,space heating,etc - and complying with IEE & PME or CEW Regulations earthing & bonding wise. The mains supplied were usually 3ph 4wire star 415V .
2) The Station's "Dirty" Earth :- All rotating machinery, pumps, compressors, s/by gennies etc,installed in an annex or separate building, had it's own dedicated earth. 3) Each Aerial had it's own Earth Matt(Woven Copper Mesh),buried adjacent or under the Aerial pole or mast. All these Matts could be bonded together underground - depending on local earth conductivity conditions. NONE of these 3 "Earths" were connected to another! This configuration proved for many years to be the best & safest for transmisson & reception purposes. Refering to choice of Star or Delta mains supplies - "Delta" is dedicated to 3phase 11 & 33KV(or other HV voltages) overhead networks or u/g supplies to sub-station's primary windings. When required for rotating machinery star/delta switchgear is used. After the supply has been dropped to LV voltages from the rural transformer or urban sub-station's secondary windings, the supplies are distributed in "Star" configuration. Some inbalance will always occur, but with experience & applied maths - distribution engineers always seem to keep this to a minimum, when designing or modifying LV distribution networks. Mind you, they are usually pretty hot on ensuring that commercial premise's have the correct Power Factor correction devices installed. Regards, David |
22nd Jul 2008, 12:54 pm | #26 | |
Dekatron
Join Date: Jul 2007
Location: Penrith, Cumbria, UK.
Posts: 3,687
|
Re: PME and RF Galvanic Isolation
Quote:
Our VLF stations have manhole lids bonded to manhole surrounds, bonded fences, gates and other extraneous metalwork. I remember at Droitwich in the 1980's there being some 240V 60W lamps between two adjacent transmitter earths; they glowed brilliantly sometimes! I can touch a key to the steel e-LORAN cabin and the earth busbar to which it is bonded a couple of metres away, and demodulate ('rusty bolt effect'), producing the distinctive 'tikkatikkatikkatik...'
__________________
Regds, Russell W. B. G4YLI. |
|