Originally Posted by budkor22 View Post
Ah... MET. If it is connected to the water pipe, then there would be connectivity between the wall socket's earth point and the water pipes.

But there is NO connectivity. I have checked a few wall sockets on the walls. No connection.
But when you say "the water pipes", we have already agreed that some of your piping somewhere contains plastic couplings. Hence, no connectivity.

What you need to do now is to check for conductivity between one of those wall socket's earth point and the metal of the metal pipe that brings water into your house at the point where it enters your house. Since that pipe will be at 'electrical earth' - or most certainly should be, since it is metal and will be buried in the ground - I think you should see a low resistance between it and the E pin of a wall socket.

Let us know if that is - or isn't the case. Thanks.