Hi Al, in power system practice it is nor unknown for a CT sec to become disconnected on a metering application. The usual trick was to fit a voltage dependent resistor (varistor, etc across the terminals and heatsink this device. Quite a bit of power can be dissipated in this device and it was normal to fit a latching thermal switch onto the heatsink with spare contact to operate an alarm.
Note that a zener will not work well in this position