I made a useful soft start unit for a large transformer.
It is a relatively simple matter to insert a series resistance for starting that is bypassed by a relay after a short time. However as has already been said, that leaves the risk that a failure of the relay or timer would leave the resistance in circuit indefinitely with consequent risk of fire.
I resolved this by using a standard electric kettle as the resistance, this is connected in series with the transformer for about a second and then bypassed.
Any failure that leaves the kettle connected continually can do no worse than boil the contents and then trigger the auto shut off of the kettle.
A 1KW or a 3KW kettle may be selected according to the size of the load.
|