Default Re: "Elevated ground" Good idea?

25A at less than 100 milliohms corresponds to less than 2.5V between chassis and plug pin. The PB3510-E3/45 diode pack would pass that test. It might even pass it with two diodes in series.

EDIT: I don't think the 10 ohm resistor should be fusible should it ? We want the earthing circuitry to blow the protective fuse, not the other way round.

Cheers,

GJ