Default Re: Neon tester vs dodgy wiring

Chris, Glyn said he earthed the switch via a milliameter and 10ma was drawn and all was well except the other switches still showed leakage. Hence my saying that if 3 of the switch plates were connected to earth and leaking 10ma each then that would be the trip current of a domestic RCD.