Default Re: Isolator Transformer Query

Quote:
Originally Posted by woodchips View Post
Doesn't seem to have been mentioned but don't leave the secondary of a mains isolating transformer floating. Why? if you earth one side then you can use an RCD before you start holding the wires, get the considerable protection these afford if you do dob your finger where it shouldn't.
Doing that means it is no longer an isolating transformer!
If floating then touching either secondary wire, or indeed any part of the connected circuit, has little effect because there is no solid path to earth - something that earthing it totally ruins! It only kills you if you touch both wires - something that is also lethal with the mains and is the situation where the RCD just sits and watches you die.
GMB is offline